Hey there,
we were just re-cabling some of the power cords on our DS4243 shelfs with 4 PSUs and 24x 15k 600GB SAS.
When I power down one of the 4 available PSUs in the DS4243, I get the following messages in system log and autosupports are generated:
Wed Feb 6 19:28:15 CET [barricade:ses.status.psError:CRITICAL]: DS4243 (S/N SHJHU000000055F) shelf 2 on channel 0a power error for Power supply 4: critical status; power supply failed. This module is on the rear side of the shelf, at the bottom right.
Wed Feb 6 19:28:15 CET [barricade:ses.status.volError:CRITICAL]: DS4243 (S/N SHJHU000000055F) shelf 2 on channel 0a voltage error for Voltage sensor 8: unrecoverable error. This module is on the rear side of the shelf, at the lower right, on the power supply.
Wed Feb 6 19:28:15 CET [barricade:ses.psu.powerReqError:CRITICAL]: Not enough power supplies are present in channel 0a disk shelf 2 to satisfy disk drive and shelf power requirements.
Wed Feb 6 19:28:15 CET [barricade:monitor.shelf.fault:CRITICAL]: Fault reported on disk storage shelf attached to channel 0a. Please check fans, power supplies, disks, and temperature sensors.
Wed Feb 6 19:28:15 CET [barricade:callhome.shlf.fault:error]: Call home for SHELF_FAULT
Wed Feb 6 19:28:15 CET [barricade:monitor.shelf.configError:CRITICAL]: Enclosure services has detected an error in access to shelves or shelf configuration 0a.
Wed Feb 6 19:28:15 CET [barricade:callhome.config:warning]: Call home for CONFIGURATION_ERROR
Wed Feb 6 19:29:00 CET [barricade:monitor.globalStatus.critical:CRITICAL]: Disk shelf fault. Disk shelf configuration error.
Wed Feb 6 19:29:11 CET [barricade:ses.status.psInfo:info]: DS4243 (S/N SHJHU000000055F) shelf 2 on channel 0a power supply information for Power supply 4: normal status.
Wed Feb 6 19:29:11 CET [barricade:ses.status.volInfo:info]: DS4243 (S/N SHJHU000000055F) shelf 2 on channel 0a voltage information for Voltage sensor 8: normal status.
Wed Feb 6 19:29:11 CET [barricade:monitor.shelf.fault.ok:info]: Fault previously reported on disk storage shelf attached to channel 0a has been corrected.
Wed Feb 6 19:29:11 CET [barricade:monitor.shelf.configError.ok:info]: Enclosure services-detected configuration error has been corrected on channel 0a.
Wed Feb 6 19:30:00 CET [barricade:monitor.globalStatus.ok:info]: The system's global status is normal.
Why exactly does it think that there are not enough power supplies present if I just shut down one of them? I was under the assumption that a full SAS shelf can work with 2 PSUs and a full SATA shelf can work with 1 PSU without problems. Am I wrong?
Nothing happend to the filers, no takeover, no errors, etc., but the message in the logs puzzles me.
Thanks && bye,
Alexander Griesser
System-Administrator
ANEXIA Internetdienstleistungs GmbH
Telefon: +43-463-208501-320
Telefax: +43-463-208501-500
E-Mail: ag@anexia.at mailto:ag@anexia.at
Web: http://www.anexia.at http://www.anexia.at
Anschrift Hauptsitz Klagenfurt: Feldkirchnerstraße 140, 9020 Klagenfurt
Geschäftsführer: Alexander Windbichler
Firmenbuch: FN 289918a | Gerichtsstand: Klagenfurt | UID-Nummer: AT U63216601
Hi Alexander,
You remember correctly, here's what should happen:
Type
PSUs
Expected Behavior
SAS
4
Normal operation. All disks will spin up at the same time.
3
Staggered disk spin-up. Six drives per column (four columns) will spin up at a time with 12-second intervals between each column.
2
Staggered disk spin-up as above.
1
The shelf will still function but with several issues. Any drives that are currently powered up when reduced to one PSU will continue to function. From a cold boot, some drives (undetermined) will not spin up due to a lack of power once a certain number of drives have spun up. This is an unsupported operating condition.
SATA
4
Normal operation. All disks will spin up at the same time.
3
Staggered disk spin-up. Six drives per column (four columns) will spin up at a time with 12-second intervals between each column.
2
Staggered disk spin-up as above.
1
Staggered disk spin-up with one difference. The first three columns, six disks each, will spin up with the normal 12-second interval. The fourth column will spin up five of six disk drives with the sixth drive (bay 23) spinning up 12seconds later.
Nevertheless I'd also expect an AutoSupport, since you *do* want a replacement PSU if one actually breaks. You might think about sending NetApp a options autosupport.doit "We're going to do some shelf maintenance" ... ;-)
Greetings from up North (Nordfriesland)
Sebastian
On 06.02.2013 19:43, Alexander Griesser wrote:
Hey there,
we were just re-cabling some of the power cords on our DS4243 shelfs with 4 PSUs and 24x 15k 600GB SAS.
When I power down one of the 4 available PSUs in the DS4243, I get the following messages in system log and autosupports are generated:
Wed Feb 6 19:28:15 CET [barricade:ses.status.psError:CRITICAL]: DS4243 (S/N SHJHU000000055F) shelf 2 on channel 0a power error for Power supply 4: critical status; power supply failed. This module is on the rear side of the shelf, at the bottom right.
Wed Feb 6 19:28:15 CET [barricade:ses.status.volError:CRITICAL]: DS4243 (S/N SHJHU000000055F) shelf 2 on channel 0a voltage error for Voltage sensor 8: unrecoverable error. This module is on the rear side of the shelf, at the lower right, on the power supply.
Wed Feb 6 19:28:15 CET [barricade:ses.psu.powerReqError:CRITICAL]: *Not enough power supplies are present*in channel 0a disk shelf 2 to satisfy disk drive and shelf power requirements.
Wed Feb 6 19:28:15 CET [barricade:monitor.shelf.fault:CRITICAL]: Fault reported on disk storage shelf attached to channel 0a. Please check fans, power supplies, disks, and temperature sensors.
Wed Feb 6 19:28:15 CET [barricade:callhome.shlf.fault:error]: Call home for SHELF_FAULT
Wed Feb 6 19:28:15 CET [barricade:monitor.shelf.configError:CRITICAL]: Enclosure services has detected an error in access to shelves or shelf configuration 0a.
Wed Feb 6 19:28:15 CET [barricade:callhome.config:warning]: Call home for CONFIGURATION_ERROR
Wed Feb 6 19:29:00 CET [barricade:monitor.globalStatus.critical:CRITICAL]: Disk shelf fault. Disk shelf configuration error.
Wed Feb 6 19:29:11 CET [barricade:ses.status.psInfo:info]: DS4243 (S/N SHJHU000000055F) shelf 2 on channel 0a power supply information for Power supply 4: normal status.
Wed Feb 6 19:29:11 CET [barricade:ses.status.volInfo:info]: DS4243 (S/N SHJHU000000055F) shelf 2 on channel 0a voltage information for Voltage sensor 8: normal status.
Wed Feb 6 19:29:11 CET [barricade:monitor.shelf.fault.ok:info]: Fault previously reported on disk storage shelf attached to channel 0a has been corrected.
Wed Feb 6 19:29:11 CET [barricade:monitor.shelf.configError.ok:info]: Enclosure services-detected configuration error has been corrected on channel 0a.
Wed Feb 6 19:30:00 CET [barricade:monitor.globalStatus.ok:info]: The system's global status is normal.
Why exactly does it think that there are not enough power supplies present if I just shut down one of them? I was under the assumption that a full SAS shelf can work with 2 PSUs and a full SATA shelf can work with 1 PSU without problems. Am I wrong?
Nothing happend to the filers, no takeover, no errors, etc., but the message in the logs puzzles me.
Thanks && bye,
*Alexander Griesser*
System-Administrator
ANEXIA Internetdienstleistungs GmbH
Telefon: +43-463-208501-320
Telefax: +43-463-208501-500
E-Mail: ag@anexia.at mailto:ag@anexia.at
Web: http://www.anexia.at
Anschrift Hauptsitz Klagenfurt: Feldkirchnerstraße 140, 9020 Klagenfurt
Geschäftsführer: Alexander Windbichler
Firmenbuch: FN 289918a | Gerichtsstand: Klagenfurt | UID-Nummer: AT U63216601
Toasters mailing list Toasters@teaparty.net http://www.teaparty.net/mailman/listinfo/toasters
Hi Sebastian,
thanks, this is a great chart - will keep it bookmarked :)
I usually do "tell" NetApp when I'm doing maintenance, but since my last OnTap update with serveral TOs and GBs I had 4 cases open and got three calls (which is great support, btw), so I figured noone is actually reading what you tell them via autosupport.doit :)
bye,
Alexander Griesser
System-Administrator
ANEXIA Internetdienstleistungs GmbH
Telefon: +43-463-208501-320
Telefax: +43-463-208501-500
E-Mail: ag@anexia.at
Web: http://www.anexia.at
Anschrift Hauptsitz Klagenfurt: Feldkirchnerstraße 140, 9020 Klagenfurt
Geschäftsführer: Alexander Windbichler
Firmenbuch: FN 289918a | Gerichtsstand: Klagenfurt | UID-Nummer: AT U63216601
Von: Sebastian Goetze [mailto:spgoetze@gmail.com] Gesendet: Mittwoch, 06. Februar 2013 22:15 An: Alexander Griesser Cc: toasters@teaparty.net Betreff: Re: Minimum PSUs required for DS4243 with 24x SAS
Hi Alexander,
You remember correctly, here's what should happen:
Type
PSUs
Expected Behavior
SAS
4
Normal operation. All disks will spin up at the same time.
3
Staggered disk spin-up. Six drives per column (four columns) will spin up at a time with 12-second intervals between each column.
2
Staggered disk spin-up as above.
1
The shelf will still function but with several issues. Any drives that are currently powered up when reduced to one PSU will continue to function. From a cold boot, some drives (undetermined) will not spin up due to a lack of power once a certain number of drives have spun up. This is an unsupported operating condition.
SATA
4
Normal operation. All disks will spin up at the same time.
3
Staggered disk spin-up. Six drives per column (four columns) will spin up at a time with 12-second intervals between each column.
2
Staggered disk spin-up as above.
1
Staggered disk spin-up with one difference. The first three columns, six disks each, will spin up with the normal 12-second interval. The fourth column will spin up five of six disk drives with the sixth drive (bay 23) spinning up 12 seconds later.
Nevertheless I'd also expect an AutoSupport, since you *do* want a replacement PSU if one actually breaks. You might think about sending NetApp a options autosupport.doit "We're going to do some shelf maintenance" ... ;-)
Greetings from up North (Nordfriesland)
Sebastian
On 06.02.2013 19:43, Alexander Griesser wrote:
Hey there,
we were just re-cabling some of the power cords on our DS4243 shelfs with 4 PSUs and 24x 15k 600GB SAS.
When I power down one of the 4 available PSUs in the DS4243, I get the following messages in system log and autosupports are generated:
Wed Feb 6 19:28:15 CET [barricade:ses.status.psError:CRITICAL]: DS4243 (S/N SHJHU000000055F) shelf 2 on channel 0a power error for Power supply 4: critical status; power supply failed. This module is on the rear side of the shelf, at the bottom right.
Wed Feb 6 19:28:15 CET [barricade:ses.status.volError:CRITICAL]: DS4243 (S/N SHJHU000000055F) shelf 2 on channel 0a voltage error for Voltage sensor 8: unrecoverable error. This module is on the rear side of the shelf, at the lower right, on the power supply.
Wed Feb 6 19:28:15 CET [barricade:ses.psu.powerReqError:CRITICAL]: Not enough power supplies are present in channel 0a disk shelf 2 to satisfy disk drive and shelf power requirements.
Wed Feb 6 19:28:15 CET [barricade:monitor.shelf.fault:CRITICAL]: Fault reported on disk storage shelf attached to channel 0a. Please check fans, power supplies, disks, and temperature sensors.
Wed Feb 6 19:28:15 CET [barricade:callhome.shlf.fault:error]: Call home for SHELF_FAULT
Wed Feb 6 19:28:15 CET [barricade:monitor.shelf.configError:CRITICAL]: Enclosure services has detected an error in access to shelves or shelf configuration 0a.
Wed Feb 6 19:28:15 CET [barricade:callhome.config:warning]: Call home for CONFIGURATION_ERROR
Wed Feb 6 19:29:00 CET [barricade:monitor.globalStatus.critical:CRITICAL]: Disk shelf fault. Disk shelf configuration error.
Wed Feb 6 19:29:11 CET [barricade:ses.status.psInfo:info]: DS4243 (S/N SHJHU000000055F) shelf 2 on channel 0a power supply information for Power supply 4: normal status.
Wed Feb 6 19:29:11 CET [barricade:ses.status.volInfo:info]: DS4243 (S/N SHJHU000000055F) shelf 2 on channel 0a voltage information for Voltage sensor 8: normal status.
Wed Feb 6 19:29:11 CET [barricade:monitor.shelf.fault.ok:info]: Fault previously reported on disk storage shelf attached to channel 0a has been corrected.
Wed Feb 6 19:29:11 CET [barricade:monitor.shelf.configError.ok:info]: Enclosure services-detected configuration error has been corrected on channel 0a.
Wed Feb 6 19:30:00 CET [barricade:monitor.globalStatus.ok:info]: The system's global status is normal.
Why exactly does it think that there are not enough power supplies present if I just shut down one of them? I was under the assumption that a full SAS shelf can work with 2 PSUs and a full SATA shelf can work with 1 PSU without problems. Am I wrong?
Nothing happend to the filers, no takeover, no errors, etc., but the message in the logs puzzles me.
Thanks && bye,
Alexander Griesser
System-Administrator
ANEXIA Internetdienstleistungs GmbH
Telefon: +43-463-208501-320
Telefax: +43-463-208501-500
E-Mail: ag@anexia.at
Web: http://www.anexia.at
Anschrift Hauptsitz Klagenfurt: Feldkirchnerstraße 140, 9020 Klagenfurt
Geschäftsführer: Alexander Windbichler
Firmenbuch: FN 289918a | Gerichtsstand: Klagenfurt | UID-Nummer: AT U63216601
_______________________________________________ Toasters mailing list Toasters@teaparty.net http://www.teaparty.net/mailman/listinfo/toasters
One way is to disable autosupport completely before your maintenance, and re-enable it afterwards.
(And if anything happens to break for-real during your maintenance, you can manually open a Case.)
Davin.
On Thu, Feb 7, 2013 at 6:10 AM, Alexander Griesser ag@anexia.at wrote:
Hi Sebastian,****
thanks, this is a great chart - will keep it bookmarked :)****
I usually do "tell" NetApp when I'm doing maintenance, but since my last OnTap update with serveral TOs and GBs I had 4 cases open and got three calls (which is great support, btw), so I figured noone is actually reading what you tell them via autosupport.doit :)****
bye,****
*Alexander Griesser*
System-Administrator****
ANEXIA Internetdienstleistungs GmbH****
Telefon: +43-463-208501-320****
Telefax: +43-463-208501-500****
E-Mail: ag@anexia.at****
Anschrift Hauptsitz Klagenfurt: Feldkirchnerstraße 140, 9020 Klagenfurt***
Geschäftsführer: Alexander Windbichler****
Firmenbuch: FN 289918a | Gerichtsstand: Klagenfurt | UID-Nummer: AT U63216601****
*Von:* Sebastian Goetze [mailto:spgoetze@gmail.com] *Gesendet:* Mittwoch, 06. Februar 2013 22:15 *An:* Alexander Griesser *Cc:* toasters@teaparty.net *Betreff:* Re: Minimum PSUs required for DS4243 with 24x SAS****
Hi Alexander,
You remember correctly, here's what should happen:****
*Type*****
*PSUs*****
*Expected Behavior*****
SAS****
4****
Normal operation. All disks will spin up at the same time.****
3****
Staggered disk spin-up. Six drives per column (four columns) will spin up at a time with 12-second intervals between each column.****
2****
Staggered disk spin-up as above.****
1****
The shelf will still function but with several issues. Any drives that are currently powered up when reduced to one PSU will continue to function. From a cold boot, some drives (undetermined) will not spin up due to a lack of power once a certain number of drives have spun up. This is an unsupported operating condition.****
SATA****
4****
Normal operation. All disks will spin up at the same time.****
3****
Staggered disk spin-up. Six drives per column (four columns) will spin up at a time with 12-second intervals between each column.****
2****
Staggered disk spin-up as above.****
1****
Staggered disk spin-up with one difference. The first three columns, six disks each, will spin up with the normal 12-second interval. The fourth column will spin up five of six disk drives with the sixth drive (bay 23) spinning up 12 seconds later.****
Nevertheless I'd also expect an AutoSupport, since you *do* want a replacement PSU if one actually breaks. You might think about sending NetApp a options autosupport.doit "We're going to do some shelf maintenance" ... ;-)
Greetings from up North (Nordfriesland)
Sebastian****
On 06.02.2013 19:43, Alexander Griesser wrote:****
Hey there,****
we were just re-cabling some of the power cords on our DS4243 shelfs with 4 PSUs and 24x 15k 600GB SAS.****
When I power down one of the 4 available PSUs in the DS4243, I get the following messages in system log and autosupports are generated:****
Wed Feb 6 19:28:15 CET [barricade:ses.status.psError:CRITICAL]: DS4243 (S/N SHJHU000000055F) shelf 2 on channel 0a power error for Power supply 4: critical status; power supply failed. This module is on the rear side of the shelf, at the bottom right.****
Wed Feb 6 19:28:15 CET [barricade:ses.status.volError:CRITICAL]: DS4243 (S/N SHJHU000000055F) shelf 2 on channel 0a voltage error for Voltage sensor 8: unrecoverable error. This module is on the rear side of the shelf, at the lower right, on the power supply.****
Wed Feb 6 19:28:15 CET [barricade:ses.psu.powerReqError:CRITICAL]: *Not enough power supplies are present* in channel 0a disk shelf 2 to satisfy disk drive and shelf power requirements.****
Wed Feb 6 19:28:15 CET [barricade:monitor.shelf.fault:CRITICAL]: Fault reported on disk storage shelf attached to channel 0a. Please check fans, power supplies, disks, and temperature sensors.****
Wed Feb 6 19:28:15 CET [barricade:callhome.shlf.fault:error]: Call home for SHELF_FAULT****
Wed Feb 6 19:28:15 CET [barricade:monitor.shelf.configError:CRITICAL]: Enclosure services has detected an error in access to shelves or shelf configuration 0a.****
Wed Feb 6 19:28:15 CET [barricade:callhome.config:warning]: Call home for CONFIGURATION_ERROR****
Wed Feb 6 19:29:00 CET [barricade:monitor.globalStatus.critical:CRITICAL]: Disk shelf fault. Disk shelf configuration error.****
Wed Feb 6 19:29:11 CET [barricade:ses.status.psInfo:info]: DS4243 (S/N SHJHU000000055F) shelf 2 on channel 0a power supply information for Power supply 4: normal status.****
Wed Feb 6 19:29:11 CET [barricade:ses.status.volInfo:info]: DS4243 (S/N SHJHU000000055F) shelf 2 on channel 0a voltage information for Voltage sensor 8: normal status.****
Wed Feb 6 19:29:11 CET [barricade:monitor.shelf.fault.ok:info]: Fault previously reported on disk storage shelf attached to channel 0a has been corrected.****
Wed Feb 6 19:29:11 CET [barricade:monitor.shelf.configError.ok:info]: Enclosure services-detected configuration error has been corrected on channel 0a.****
Wed Feb 6 19:30:00 CET [barricade:monitor.globalStatus.ok:info]: The system's global status is normal.****
Why exactly does it think that there are not enough power supplies present if I just shut down one of them? I was under the assumption that a full SAS shelf can work with 2 PSUs and a full SATA shelf can work with 1 PSU without problems. Am I wrong?****
Nothing happend to the filers, no takeover, no errors, etc., but the message in the logs puzzles me.****
Thanks && bye,****
*Alexander Griesser*****
System-Administrator****
ANEXIA Internetdienstleistungs GmbH****
Telefon: +43-463-208501-320****
Telefax: +43-463-208501-500****
E-Mail: ag@anexia.at****
Anschrift Hauptsitz Klagenfurt: Feldkirchnerstraße 140, 9020 Klagenfurt***
Geschäftsführer: Alexander Windbichler****
Firmenbuch: FN 289918a | Gerichtsstand: Klagenfurt | UID-Nummer: AT U63216601****
_______________________________________________****
Toasters mailing list****
Toasters@teaparty.net****
http://www.teaparty.net/mailman/listinfo/toasters****
Toasters mailing list Toasters@teaparty.net http://www.teaparty.net/mailman/listinfo/toasters