Guys,
We're in the process of starting to migrate from some 3140s running 7.3.6 to a 3220 cluster running 8.1.2, or whatever the latest release is. Going from 3.5 racks down to just 1 rack, woohoo! But I'm short of 30amp power plugs in my data center. So my plan is to drop one of my 3140s down to just two 30A circuits so I can bring up the 3220 cluster with fully redundant power.
I know I need to turn off autosupport while this is happening, though I'd like to just turn off warning about power problems and keep auto support going for disk failures.
Any suggestions or comments?
Thanks, John
Hi John,
there are serveral things that cannot be configured here (at least that's what I've always been told when asking questions like this). I do have filers which are low on spares intentionally f.ex., but according to NetApp (at least according to the tech that handled my autosupport case) there's no option of telling the filer to not moan about a low spares condition.
We were doing UPS maintenance some weeks ago and I forgot to disable auto support before doing that and so a handful of autosupport tickets got created and I did also ask if it's possible to disable AS warnings for power conditions, but just got the same answer there: Not possible.
So if there are ways to fine-tune what gets sent via autosupport, I'd love to hear them too :)
Bye,
Alexander Griesser System-Administrator
ANEXIA Internetdienstleistungs GmbH
Telefon: +43-463-208501-320 Telefax: +43-463-208501-500
E-Mail: ag@anexia.at Web: http://www.anexia.at
Anschrift Hauptsitz Klagenfurt: Feldkirchnerstraße 140, 9020 Klagenfurt Geschäftsführer: Alexander Windbichler Firmenbuch: FN 289918a | Gerichtsstand: Klagenfurt | UID-Nummer: AT U63216601
-----Ursprüngliche Nachricht----- Von: toasters-bounces@teaparty.net [mailto:toasters-bounces@teaparty.net] Im Auftrag von John Stoffel Gesendet: Mittwoch, 24. April 2013 18:07 An: toasters@teaparty.net Betreff: Running on non-redundant power
Guys,
We're in the process of starting to migrate from some 3140s running 7.3.6 to a 3220 cluster running 8.1.2, or whatever the latest release is. Going from 3.5 racks down to just 1 rack, woohoo! But I'm short of 30amp power plugs in my data center. So my plan is to drop one of my 3140s down to just two 30A circuits so I can bring up the 3220 cluster with fully redundant power.
I know I need to turn off autosupport while this is happening, though I'd like to just turn off warning about power problems and keep auto support going for disk failures.
Any suggestions or comments?
Thanks, John _______________________________________________ Toasters mailing list Toasters@teaparty.net http://www.teaparty.net/mailman/listinfo/toasters
A lame suggestion is to turn autosupport off for Netapp (look for netapp addressing in options autosuport and disable). If you are using DFM/Operations Manager/OnCommand/next marketing term for internal monitoring, you will know when a disk fails.. If you get a disk failure, you can call, give them the messages file and they should send out a replacement...
Just a suggestion.
-----Original Message----- From: toasters-bounces@teaparty.net [mailto:toasters-bounces@teaparty.net] On Behalf Of Alexander Griesser Sent: Wednesday, April 24, 2013 9:11 AM To: John Stoffel; toasters@teaparty.net Subject: AW: Running on non-redundant power
Hi John,
there are serveral things that cannot be configured here (at least that's what I've always been told when asking questions like this). I do have filers which are low on spares intentionally f.ex., but according to NetApp (at least according to the tech that handled my autosupport case) there's no option of telling the filer to not moan about a low spares condition.
We were doing UPS maintenance some weeks ago and I forgot to disable auto support before doing that and so a handful of autosupport tickets got created and I did also ask if it's possible to disable AS warnings for power conditions, but just got the same answer there: Not possible.
So if there are ways to fine-tune what gets sent via autosupport, I'd love to hear them too :)
Bye,
Alexander Griesser System-Administrator
ANEXIA Internetdienstleistungs GmbH
Telefon: +43-463-208501-320 Telefax: +43-463-208501-500
E-Mail: ag@anexia.at Web: http://www.anexia.at
Anschrift Hauptsitz Klagenfurt: Feldkirchnerstraße 140, 9020 Klagenfurt Geschäftsführer: Alexander Windbichler Firmenbuch: FN 289918a | Gerichtsstand: Klagenfurt | UID-Nummer: AT U63216601
-----Ursprüngliche Nachricht----- Von: toasters-bounces@teaparty.net [mailto:toasters-bounces@teaparty.net] Im Auftrag von John Stoffel Gesendet: Mittwoch, 24. April 2013 18:07 An: toasters@teaparty.net Betreff: Running on non-redundant power
Guys,
We're in the process of starting to migrate from some 3140s running 7.3.6 to a 3220 cluster running 8.1.2, or whatever the latest release is. Going from 3.5 racks down to just 1 rack, woohoo! But I'm short of 30amp power plugs in my data center. So my plan is to drop one of my 3140s down to just two 30A circuits so I can bring up the 3220 cluster with fully redundant power.
I know I need to turn off autosupport while this is happening, though I'd like to just turn off warning about power problems and keep auto support going for disk failures.
Any suggestions or comments?
Thanks, John _______________________________________________ Toasters mailing list Toasters@teaparty.net http://www.teaparty.net/mailman/listinfo/toasters
_______________________________________________ Toasters mailing list Toasters@teaparty.net http://www.teaparty.net/mailman/listinfo/toasters
why bother at all...
for just a few buck you can go out and get some "Y" power cables (C13/C14) and fake the NetApp gear into thinking it is fully powered.
I have done that ....so many times.... before.
--tmac
*Tim McCarthy* *Principal Consultant*
Clustered ONTAP Clustered ONTAP NCDA ID: XK7R3GEKC1QQ2LVD RHCE5 805007643429572 NCSIE ID: C14QPHE21FR4YWD4 Expires: 08 November 2014 Expires w/release of RHEL7 Expires: 08 November 2014
On Wed, Apr 24, 2013 at 12:26 PM, Klise, Steve klises@sutterhealth.orgwrote:
A lame suggestion is to turn autosupport off for Netapp (look for netapp addressing in options autosuport and disable). If you are using DFM/Operations Manager/OnCommand/next marketing term for internal monitoring, you will know when a disk fails.. If you get a disk failure, you can call, give them the messages file and they should send out a replacement...
Just a suggestion.
-----Original Message----- From: toasters-bounces@teaparty.net [mailto:toasters-bounces@teaparty.net] On Behalf Of Alexander Griesser Sent: Wednesday, April 24, 2013 9:11 AM To: John Stoffel; toasters@teaparty.net Subject: AW: Running on non-redundant power
Hi John,
there are serveral things that cannot be configured here (at least that's what I've always been told when asking questions like this). I do have filers which are low on spares intentionally f.ex., but according to NetApp (at least according to the tech that handled my autosupport case) there's no option of telling the filer to not moan about a low spares condition.
We were doing UPS maintenance some weeks ago and I forgot to disable auto support before doing that and so a handful of autosupport tickets got created and I did also ask if it's possible to disable AS warnings for power conditions, but just got the same answer there: Not possible.
So if there are ways to fine-tune what gets sent via autosupport, I'd love to hear them too :)
Bye,
Alexander Griesser System-Administrator
ANEXIA Internetdienstleistungs GmbH
Telefon: +43-463-208501-320 Telefax: +43-463-208501-500
E-Mail: ag@anexia.at Web: http://www.anexia.at
Anschrift Hauptsitz Klagenfurt: Feldkirchnerstraße 140, 9020 Klagenfurt Geschäftsführer: Alexander Windbichler Firmenbuch: FN 289918a | Gerichtsstand: Klagenfurt | UID-Nummer: AT U63216601
-----Ursprüngliche Nachricht----- Von: toasters-bounces@teaparty.net [mailto:toasters-bounces@teaparty.net] Im Auftrag von John Stoffel Gesendet: Mittwoch, 24. April 2013 18:07 An: toasters@teaparty.net Betreff: Running on non-redundant power
Guys,
We're in the process of starting to migrate from some 3140s running 7.3.6 to a 3220 cluster running 8.1.2, or whatever the latest release is. Going from 3.5 racks down to just 1 rack, woohoo! But I'm short of 30amp power plugs in my data center. So my plan is to drop one of my 3140s down to just two 30A circuits so I can bring up the 3220 cluster with fully redundant power.
I know I need to turn off autosupport while this is happening, though I'd like to just turn off warning about power problems and keep auto support going for disk failures.
Any suggestions or comments?
Thanks, John _______________________________________________ Toasters mailing list Toasters@teaparty.net http://www.teaparty.net/mailman/listinfo/toasters
Toasters mailing list Toasters@teaparty.net http://www.teaparty.net/mailman/listinfo/toasters
Toasters mailing list Toasters@teaparty.net http://www.teaparty.net/mailman/listinfo/toasters
You can tell support you have a window coming, to ignore power notices.
On Wed, Apr 24, 2013 at 12:21 PM, tmac tmacmd@gmail.com wrote:
why bother at all...
for just a few buck you can go out and get some "Y" power cables (C13/C14) and fake the NetApp gear into thinking it is fully powered.
I have done that ....so many times.... before.
--tmac
*Tim McCarthy* *Principal Consultant*
Clustered ONTAP Clustered ONTAP NCDA ID: XK7R3GEKC1QQ2LVD RHCE5 805007643429572 NCSIE ID: C14QPHE21FR4YWD4 Expires: 08 November 2014 Expires w/release of RHEL7 Expires: 08 November 2014
On Wed, Apr 24, 2013 at 12:26 PM, Klise, Steve klises@sutterhealth.orgwrote:
A lame suggestion is to turn autosupport off for Netapp (look for netapp addressing in options autosuport and disable). If you are using DFM/Operations Manager/OnCommand/next marketing term for internal monitoring, you will know when a disk fails.. If you get a disk failure, you can call, give them the messages file and they should send out a replacement...
Just a suggestion.
-----Original Message----- From: toasters-bounces@teaparty.net [mailto:toasters-bounces@teaparty.net] On Behalf Of Alexander Griesser Sent: Wednesday, April 24, 2013 9:11 AM To: John Stoffel; toasters@teaparty.net Subject: AW: Running on non-redundant power
Hi John,
there are serveral things that cannot be configured here (at least that's what I've always been told when asking questions like this). I do have filers which are low on spares intentionally f.ex., but according to NetApp (at least according to the tech that handled my autosupport case) there's no option of telling the filer to not moan about a low spares condition.
We were doing UPS maintenance some weeks ago and I forgot to disable auto support before doing that and so a handful of autosupport tickets got created and I did also ask if it's possible to disable AS warnings for power conditions, but just got the same answer there: Not possible.
So if there are ways to fine-tune what gets sent via autosupport, I'd love to hear them too :)
Bye,
Alexander Griesser System-Administrator
ANEXIA Internetdienstleistungs GmbH
Telefon: +43-463-208501-320 Telefax: +43-463-208501-500
E-Mail: ag@anexia.at Web: http://www.anexia.at
Anschrift Hauptsitz Klagenfurt: Feldkirchnerstraße 140, 9020 Klagenfurt Geschäftsführer: Alexander Windbichler Firmenbuch: FN 289918a | Gerichtsstand: Klagenfurt | UID-Nummer: AT U63216601
-----Ursprüngliche Nachricht----- Von: toasters-bounces@teaparty.net [mailto:toasters-bounces@teaparty.net] Im Auftrag von John Stoffel Gesendet: Mittwoch, 24. April 2013 18:07 An: toasters@teaparty.net Betreff: Running on non-redundant power
Guys,
We're in the process of starting to migrate from some 3140s running 7.3.6 to a 3220 cluster running 8.1.2, or whatever the latest release is. Going from 3.5 racks down to just 1 rack, woohoo! But I'm short of 30amp power plugs in my data center. So my plan is to drop one of my 3140s down to just two 30A circuits so I can bring up the 3220 cluster with fully redundant power.
I know I need to turn off autosupport while this is happening, though I'd like to just turn off warning about power problems and keep auto support going for disk failures.
Any suggestions or comments?
Thanks, John _______________________________________________ Toasters mailing list Toasters@teaparty.net http://www.teaparty.net/mailman/listinfo/toasters
Toasters mailing list Toasters@teaparty.net http://www.teaparty.net/mailman/listinfo/toasters
Toasters mailing list Toasters@teaparty.net http://www.teaparty.net/mailman/listinfo/toasters
Toasters mailing list Toasters@teaparty.net http://www.teaparty.net/mailman/listinfo/toasters
tmac> why bother at all... for just a few buck you can go out and get tmac> some "Y" power cables (C13/C14) and fake the NetApp gear into tmac> thinking it is fully powered.
tmac> I have done that ....so many times.... before.
Duh... what a great idea. My other thought had been to just turn off the power switches on the un-powered side to silence the alarm as well.
And those cords are cheap too! Only $7 each for 3 footers.
http://rackmountpdu.com/Category/150-c14-to-c13-splitter-power-cords.aspx
John
Hi Alexander,
slightly off-topic, but I couldn't resist:
from the documentation: *options raid.min_spare_count* Specifies the minimum number of spare drives required to avoid warnings for low spares. If there are at least raid.min_spare_count spare drives that are appropriate replacements for any filesystem disk, then there will be no warnings for low spares. This option can be set from 0 to 4. The default setting is 1. Setting this option to 0 means that there will be no warnings for low spares even if there are no spares available. This option can be set to 0 only on systems with 16 or fewer attached drives and that are running with RAID-DP aggregates. A setting of 0 is not allowed on systems with RAID4 aggregates.
It's e.g. mentioned also in the Storage Subsystem Technical FAQ under the heading 'WHAT IS THE RECOMMENDED AGGREGATE AND RAID GROUP CONFIGURATION FOR A FAS2020 OR FAS2040 SYSTEM USING ONLY 12 INTERNAL DRIVES?' for an asymmetric configuration...
Mind you: There are certain conditions to be met to be able to set this to 0 which you might not have fulfilled...
Hope that helps
Sebastian
On 24.04.2013 18:10, Alexander Griesser wrote:
Hi John,
there are serveral things that cannot be configured here (at least that's what I've always been told when asking questions like this). I do have filers which are low on spares intentionally f.ex., but according to NetApp (at least according to the tech that handled my autosupport case) there's no option of telling the filer to not moan about a low spares condition.
We were doing UPS maintenance some weeks ago and I forgot to disable auto support before doing that and so a handful of autosupport tickets got created and I did also ask if it's possible to disable AS warnings for power conditions, but just got the same answer there: Not possible.
So if there are ways to fine-tune what gets sent via autosupport, I'd love to hear them too :)
Bye,
Alexander Griesser System-Administrator
ANEXIA Internetdienstleistungs GmbH
Telefon: +43-463-208501-320 Telefax: +43-463-208501-500
E-Mail: ag@anexia.at Web: http://www.anexia.at
Anschrift Hauptsitz Klagenfurt: Feldkirchnerstraße 140, 9020 Klagenfurt Geschäftsführer: Alexander Windbichler Firmenbuch: FN 289918a | Gerichtsstand: Klagenfurt | UID-Nummer: AT U63216601
-----Ursprüngliche Nachricht----- Von: toasters-bounces@teaparty.net [mailto:toasters-bounces@teaparty.net] Im Auftrag von John Stoffel Gesendet: Mittwoch, 24. April 2013 18:07 An: toasters@teaparty.net Betreff: Running on non-redundant power
Guys,
We're in the process of starting to migrate from some 3140s running 7.3.6 to a 3220 cluster running 8.1.2, or whatever the latest release is. Going from 3.5 racks down to just 1 rack, woohoo! But I'm short of 30amp power plugs in my data center. So my plan is to drop one of my 3140s down to just two 30A circuits so I can bring up the 3220 cluster with fully redundant power.
I know I need to turn off autosupport while this is happening, though I'd like to just turn off warning about power problems and keep auto support going for disk failures.
Any suggestions or comments?
Thanks, John _______________________________________________ Toasters mailing list Toasters@teaparty.net http://www.teaparty.net/mailman/listinfo/toasters
Toasters mailing list Toasters@teaparty.net http://www.teaparty.net/mailman/listinfo/toasters
I think that spare option is only for certain versions of on tap.
Jack Sent from my Verizon Wireless BlackBerry
-----Original Message----- From: Sebastian Goetze spgoetze@gmail.com Sender: toasters-bounces@teaparty.net Date: Wed, 24 Apr 2013 21:46:34 To: Alexander Griesserag@anexia.at; John Stoffeljohn.stoffel@taec.toshiba.com; toasters@teaparty.nettoasters@teaparty.net Subject: Re: Running on non-redundant power -> Low Spares...
_______________________________________________ Toasters mailing list Toasters@teaparty.net http://www.teaparty.net/mailman/listinfo/toasters
Hi Sebastian,
thanks, that worked :)
bye,
Alexander Griesser System-Administrator
ANEXIA Internetdienstleistungs GmbH
Telefon: +43-463-208501-320 Telefax: +43-463-208501-500
E-Mail: ag@anexia.atmailto:ag@anexia.at Web: http://www.anexia.at
Anschrift Hauptsitz Klagenfurt: Feldkirchnerstraße 140, 9020 Klagenfurt Geschäftsführer: Alexander Windbichler Firmenbuch: FN 289918a | Gerichtsstand: Klagenfurt | UID-Nummer: AT U63216601
Von: Sebastian Goetze [mailto:spgoetze@gmail.com] Gesendet: Mittwoch, 24. April 2013 21:47 An: Alexander Griesser; John Stoffel; toasters@teaparty.net Betreff: Re: Running on non-redundant power -> Low Spares...
Hi Alexander,
slightly off-topic, but I couldn't resist:
from the documentation: options raid.min_spare_count Specifies the minimum number of spare drives required to avoid warnings for low spares. If there are at least raid.min_spare_count spare drives that are appropriate replacements for any filesystem disk, then there will be no warnings for low spares. This option can be set from 0 to 4. The default setting is 1. Setting this option to 0 means that there will be no warnings for low spares even if there are no spares available. This option can be set to 0 only on systems with 16 or fewer attached drives and that are running with RAID-DP aggregates. A setting of 0 is not allowed on systems with RAID4 aggregates.
It's e.g. mentioned also in the Storage Subsystem Technical FAQ under the heading 'WHAT IS THE RECOMMENDED AGGREGATE AND RAID GROUP CONFIGURATION FOR A FAS2020 OR FAS2040 SYSTEM USING ONLY 12 INTERNAL DRIVES?' for an asymmetric configuration...
Mind you: There are certain conditions to be met to be able to set this to 0 which you might not have fulfilled...
Hope that helps
Sebastian
On 24.04.2013 18:10, Alexander Griesser wrote:
Hi John,
there are serveral things that cannot be configured here (at least that's what I've always been told when asking questions like this).
I do have filers which are low on spares intentionally f.ex., but according to NetApp (at least according to the tech that handled my autosupport case) there's no option of telling the filer to not moan about a low spares condition.
We were doing UPS maintenance some weeks ago and I forgot to disable auto support before doing that and so a handful of autosupport tickets got created and I did also ask if it's possible to disable AS warnings for power conditions, but just got the same answer there: Not possible.
So if there are ways to fine-tune what gets sent via autosupport, I'd love to hear them too :)
Bye,
Alexander Griesser
System-Administrator
ANEXIA Internetdienstleistungs GmbH
Telefon: +43-463-208501-320
Telefax: +43-463-208501-500
E-Mail: ag@anexia.atmailto:ag@anexia.at
Web: http://www.anexia.at
Anschrift Hauptsitz Klagenfurt: Feldkirchnerstraße 140, 9020 Klagenfurt
Geschäftsführer: Alexander Windbichler
Firmenbuch: FN 289918a | Gerichtsstand: Klagenfurt | UID-Nummer: AT U63216601
-----Ursprüngliche Nachricht-----
Von: toasters-bounces@teaparty.netmailto:toasters-bounces@teaparty.net [mailto:toasters-bounces@teaparty.net] Im Auftrag von John Stoffel
Gesendet: Mittwoch, 24. April 2013 18:07
An: toasters@teaparty.netmailto:toasters@teaparty.net
Betreff: Running on non-redundant power
Guys,
We're in the process of starting to migrate from some 3140s running
7.3.6 to a 3220 cluster running 8.1.2, or whatever the latest release
is. Going from 3.5 racks down to just 1 rack, woohoo! But I'm short
of 30amp power plugs in my data center. So my plan is to drop one of
my 3140s down to just two 30A circuits so I can bring up the 3220
cluster with fully redundant power.
I know I need to turn off autosupport while this is happening, though
I'd like to just turn off warning about power problems and keep auto
support going for disk failures.
Any suggestions or comments?
Thanks,
John
_______________________________________________
Toasters mailing list
Toasters@teaparty.netmailto:Toasters@teaparty.net
http://www.teaparty.net/mailman/listinfo/toasters
_______________________________________________
Toasters mailing list
Toasters@teaparty.netmailto:Toasters@teaparty.net